ABB AC500 PM582 V1.2

Begonnen von xroi, 01. August 2011, 08:03:44

Vorheriges Thema - Nächstes Thema

0 Mitglieder und 1 Gast betrachten dieses Thema.

xroi

Hello!

I'm using ABB controller AC500 PM582 (Target version V1.2). CoDeSys v.2.3.
There are a few things that you can help me.
1. oscat.lib takes too much POU's - and I can't enlarge them! Request sent to manufacturer.
2. In oscat.lib library there are repeated elements like in the standard libraries, for example, INT_To_BCD, BCD_TO_INT (look at util.lib). So, it's necessary to delete something... :( :( :'(

What to do?
Is it possible to divide the oscat.lib library into several small and simple libraries, which can be efficiently used?
But if you have interesting and cool solution please help me...)))

hihi

Hi,

I've the same issue, maximum number of POUs exceeded ...
Would it be possible to split up the lib? or is there a way of disabling some of the POUs which I don't use?

thank you for the support

hihi

Hi All,

Got it, I've found a way to disable the POU's I didnt use ... newbie ...

cheers,