DCF77 signal

Begonnen von SweElite, 29. Januar 2009, 11:04:34

Vorheriges Thema - Nächstes Thema

0 Mitglieder und 2 Gäste betrachten dieses Thema.

SweElite

Hello !

Can someone tell me how i can use the DCF77 signal. What kind of module / device do i need ?

Please advice.

Christoffer

hugo

use DCF77 from the library and any commercially available DCF77 receiver.
the output of the receiver goes to the Input REC of DCF77  but be careful some receivers have a low acitve output, in this case you need to change polarity of the input REC.
You also need the have the correct input module for your PLC matching the output voltage of your receiver.

all other inputs of DCF77 can remain unconnected and it should give you time and date after approximately 2-3 minutes of received data.

SweElite

Aha..thanks alot Hugo. Any particular reciever you know works ?



Zitat von: hugo in 29. Januar 2009, 11:15:14
use DCF77 from the library and any commercially available DCF77 receiver.
the output of the receiver goes to the Input REC of DCF77  but be careful some receivers have a low acitve output, in this case you need to change polarity of the input REC.
You also need the have the correct input module for your PLC matching the output voltage of your receiver.

all other inputs of DCF77 can remain unconnected and it should give you time and date after approximately 2-3 minutes of received data.

hugo

i have used a few like conrad and others but it should make no difference which one you use, the main thing is the interface to the correct input and low or high active output of the receiver

maisanuk

I developed a few month ago a commercial receiver especially for use with PLCs. The output signal is a PNP-sytle, 24V, short circuit protected signal for the DCF function block. Supply is 24V as well.
This weeks I revised the receiver and now it kommes with proper housing. The manuall is only in German language available.
You can find some more information on my web page www.shascom.net
Rgds

maisanuk